The significance of cracks in concrete from a structural engineering perspective


2.7K

Way back in 1849, a French gardener by the name of Josef Monier invented the principle of reinforced concrete. His 1881 patent marked the start of the significant use of this new material. In the same year, Prussian engineers A. G. Wayss and M. Koenen understood the basic principle of reinforced concrete, namely that the steel absorbs all tension stresses and the concrete only provides compression resistance. The true reinforced concrete theory was born.

A cracked tension zone is always assumed in general reinforced-concrete construction design, and this condition alone does not represent a safety hazard (although there may be some concerns with regard to durability). But in the process of designing a steel anchor plate connection, this subject is clearly of greater importance, since cracks in an anchoring base material not only impair the distribution of stress resulting from loaded anchors, but also lead to the serious malfunctioning of anchors that are not suitable for this condition.

As an engineer, you are the one in charge of assuming in your design strategy whether or not the concrete is cracked in the fixing area, as well as selecting and designing the anchor plate connection accordingly. However, you must be aware that the results of this process can vary significantly depending on the initial assumption and the anchor system selected.

As a general rule, one has to assume that the concrete is cracked, unless proven otherwise (such as by conducting a thorough stress analysis or a documented visual inspection of cracks).

In order to make a well-founded decision, you might be interested in the basics of fastening into cracked concrete, which are covered in this article (the focus here is upon static conditions; we will cover seismic conditions in a future article). All references are included at the end of the page.

 

How cracked will the concrete be?

Concrete has a low tensile strength, so cracks are also expected in service conditions in flexural or tension components. Experience shows that crack widths resulting from primarily quasi-static loads (dead loads plus a fraction of live load) do not exceed the value of w95% ~ 0.3 mm to 0.4 mm. Wider cracks are to be expected under maximum permissible service loads, which reach w95%~0.5 mm to 0.6 mm [2],[3],[4].


Relative frequency of measured crack width under maximum service loads ([2],[3],[4])

 

Cracks depend on both internal and external forces

Cracks form on a reinforced member not only due to the action of forces (transferred from the fixing or other elements in the structure) but also earlier as a result of the concrete setting process (shrinkage). Additionally, stresses can occur through constraint forces due to differences in temperature, hindered deformation or foundation settlement which, in turn, might cause cracking.


If concrete is tensioned, cracks most likely will intersect the anchor

It has been observed that when cracks form in a concrete member, it is highly likely that they will intersect the anchor location directly or tangentially [1]. This occurs because higher tensile stresses exist around the anchor as a result of the hoop stresses associated with the prestressing and loading of the anchor and the stress concentration caused by the presence of the anchor hole (notch effect).


The likelihood of seeing cracks form in relation to the anchor position is very high, due to the stress concentration and discontinuity caused by the fixing itself.


The higher stress field associated with cracks reduces the load


In non-cracked concrete, a tension-loaded anchor generates a rotationally symmetric stress pattern around the anchor [1]. If the anchor is located in cracks, the tensile stresses can no longer be transferred across the crack plan and are not rotationally distributed (disturbance of the rotational stress field). This reduces the failure load in the case of concrete cone failure.

Distribution of forces in the anchorage

zone in uncracked and cracked concrete [1]


A non-cracked concrete-designed anchor can exhibit uncontrolled slip when loaded in tensioned concrete

The effect of cracking is not only on the peak load of the fixing. In fact, the load displacement behavior can also vary significantly according to the anchor's capability to respond to the notch opening. For example, torque-controlled expansion anchors that are not suitable for applications in cracked concrete can exhibit uncontrolled slip when loaded in tension in cracks. Uncontrolled displacements causing unpredictable deflections are a risk for both SLS and SLU, especially for some applications such as free-standing structures, cantilevers and rigid beam connections.

 

Schematic load displacement curves of torque-controlled anchors tested [1] in tension in cracked and non-cracked concrete

a) Anchors suitable for use in cracked concrete

b) Anchors not suitable for use in cracked concrete

 
To conclude

In general, cracks in concrete are expected, and the probable location of the cracks can be easily predicted in the anchor position, implying a reduction of the load capacity or higher deformations. We recommend that you always consider the concrete as cracked in your design, unless dealing with applications where it is clear that the concrete will never be tensioned, such as light fastening on pre-stressed concrete elements (to be proven, in any case). Otherwise, anchors qualified for use in tensioned concrete should be used to ensure safety through a proper design, while solutions for which the performance has not been assessed in this condition cannot guarantee adequate reliability.

If you want to know more about which solutions are more adequate in cracked concrete and how to execute your designs accordingly, just leave a comment here.


 

References

[1] Eligehausen R.; Mallee, R.; Silva, J.F. (2006): Anchorage in concrete construction, Ernst & Sohn, Berlin 2006

[2]Schiessl, P. (1986): Crack influence of the durability of reinforced and prestressed concrete components. Schriftenreihe des Deutschen Ausschuss für Stahlbeton, No. 370, Ernst & Sohn, Berlin 1986 (in German)

[3] Bergmeister, K. (1988): Stochastic in fixing technology based on realistic influenced parameters, Doctor Thesis, University of Innsbruck, 1988 (in German)

[4] Eligehausen, R.; Bozenhardt, A. (1989): Crack widths as measured in actual structures and conclusions for the testing of fastening elements. Report No. 1/42-89/9, Institute of Construction Materials, University of Stuttgart, August 1989

1comment on this article
Posted bySOLMAZ POURZEYNALIover 1 year ago
How the mentioned standard has considered the effect of cracked concrete in calculations?